This site is not affiliated with AGCO Inc., Duluth GA., Allis-Chalmers Co., Milwaukee, WI., or any surviving or related corporate entity. All trademarks remain the property of their respective owners. All information presented herein should be considered the result of an un-moderated public forum with no responsibility for its accuracy or usability assumed by the users and sponsors of this site or any corporate entity. | |||||
The Forum | Parts and Services | Unofficial Allis Store | Tractor Shows | Serial Numbers | History |
Frost proof yard hydrant. |
Post Reply ![]() |
Author | |
BrianC ![]() Orange Level Access ![]() Joined: 16 Jun 2011 Location: New York Points: 1619 |
![]() ![]() ![]() ![]() ![]() Posted: 04 Dec 2020 at 2:04pm |
I replaced my yard hydrant, was a Campbell, now is a Parts 2 O. The plunger in the Campbell was really stuck, so I decided to chuck the whole thing. Digging up the hole (3ft bury depth) was interesting and easy until I got to the gravel. Decided to test before back-filling the hole. The new hydrant is constantly leaking out the drain hole. The lever was very easy to shut closed, so I adjusted the set screw gripping spot on the pull rod. Now the handle's last 30 degrees needs moderate pressure to close it (5 pounds??, not a lot, I didn't want to mash the plunger). After letting it run and then shutting off, it still is "draining" from the drain hole down there 2 hours later. The instruction say 40 psi is the normal supply pressure, more will reduce lifetime on the components. I have 92 PSI water supply. What is going on? |
|
![]() |
|
Sponsored Links | |
![]() |
|
DiyDave ![]() Orange Level Access ![]() ![]() Joined: 11 Sep 2009 Location: Gambrills, MD Points: 54039 |
![]() ![]() ![]() ![]() ![]() |
I can't remember the brand I like the most.(senior moment?) painted green, it s repairable, from the top, no digging.
When replacing hydrants, I spend the money, up front, I hates diggin in the cold, seems like that's when they fail... On edit, I found the name, its a baker! see link below. 92 PSI pressure sounds pretty damn high, I think that may be your main problem... |
|
Source: Babylon Bee. Sponsored by BRAWNDO, its got what you need!
|
|
![]() |
|
mdm1 ![]() Orange Level ![]() ![]() Joined: 12 Sep 2009 Location: Onalaska, WI Points: 2677 |
![]() ![]() ![]() ![]() ![]() |
As Dave said 92 psi is way high. Most wells are 40/60. Surprised you don't have other problems.
|
|
Everything is impossible until someone does it! WD45-trip loader 1947 c w/woods belly mower, 1939 B, #3 sickle mower 1944 B, 2 1948 G's. Misc other equipment that my wife calls JUNK!
|
|
![]() |
|
DougG ![]() Orange Level ![]() Joined: 20 Sep 2009 Location: Mo Points: 8338 |
![]() ![]() ![]() ![]() ![]() |
Do you have a well or city water ? 92 lbs is way to much
|
|
![]() |
|
BrianC ![]() Orange Level Access ![]() Joined: 16 Jun 2011 Location: New York Points: 1619 |
![]() ![]() ![]() ![]() ![]() |
I looked up the Baker hydrant, that sure is constructed differently than the ones I have. I could not find the PSI rating for it. The 92psi line is 1-1/2 galvanized pipe, runs out 240 feet to garden. It is tapped before the water pressure regulator for the home. Home was converted from well system to municipal water sometime in the '90's. I bet the old shallow well system could only hit about 45psi. Thing is I like the high pressure. I can water in bigger circles, spray higher up the apple trees and such. Sounds like more plumbing or convert to dumb faucet and drain for winter. I use it for gardening only.
|
|
![]() |
|
plummerscarin ![]() Orange Level Access ![]() Joined: 22 Jun 2015 Location: ia Points: 3902 |
![]() ![]() ![]() ![]() ![]() |
92 is very high. From a code perspective, if over 80 then a pressure reducing valve would required. Some pressure to close the handle would be normal in my opinion. Also be sure there is no dirt or other objects preventing proper seal when off and there is no damage to the seat or washer.
|
|
![]() |
|
HD6GTOM ![]() Orange Level ![]() ![]() Joined: 30 Nov 2009 Location: MADISON CO IA Points: 6627 |
![]() ![]() ![]() ![]() ![]() |
We've been using Iowa hydrants since the 1960's. I I cannot remember a leaker. We have to put them down 6' here.
|
|
![]() |
|
Kansas99 ![]() Orange Level Access ![]() Joined: 26 Feb 2015 Location: W Kansas Points: 4867 |
![]() ![]() ![]() ![]() ![]() |
Interesting, hadn't heard of them but according to their site these are rated up to 125psi.
![]() |
|
"Thank you for your service Joe & the Ho"-----Joseph Stalin
|
|
![]() |
|
DiyDave ![]() Orange Level Access ![]() ![]() Joined: 11 Sep 2009 Location: Gambrills, MD Points: 54039 |
![]() ![]() ![]() ![]() ![]() |
Last one I bought a coupla years ago was around $130, IIRR, for a 7' (total length). Of course local prices will vary. I bought it at the local Drillers Service store, check them out, they may have a location, near Brian's, or you, K99...
![]() |
|
Source: Babylon Bee. Sponsored by BRAWNDO, its got what you need!
|
|
![]() |
|
FREEDGUY ![]() Orange Level Access ![]() ![]() Joined: 15 Apr 2017 Location: South West Mich Points: 5396 |
![]() ![]() ![]() ![]() ![]() |
Are you certain that whatever gauge that reads 92 PSI is accurate ?? That seem excessive from a municipality unless your first in line from their pumping station (in between filling the water tower)
![]() |
|
![]() |
|
Coke-in-MN ![]() Orange Level Access ![]() Joined: 12 Sep 2009 Location: Afton MN Points: 41979 |
![]() ![]() ![]() ![]() ![]() |
When installing the hydrants for farm use - I used a 5 gallon plastic bucket to set hydrant into , then made connections - allowed a void around the valve to allow drainage and kept the hole from getting plugged or sand getting into valve .
I would expect the seat in your hydrant valve is bad as it should seal without leakage at ANY pressure if it is working . |
|
Life lesson: If you’re being chased by a lion, you’re on a horse, to the left of you is a giraffe and on the right is a unicorn, what do you do? You stop drinking and get off the carousel.
|
|
![]() |
|
FREEDGUY ![]() Orange Level Access ![]() ![]() Joined: 15 Apr 2017 Location: South West Mich Points: 5396 |
![]() ![]() ![]() ![]() ![]() |
Have you DONE the "repair from the top" fix ?? I just CAN NOT imagine lining thigs up 4' down in murky/muddy waters ??
|
|
![]() |
|
steve(ill) ![]() Orange Level Access ![]() ![]() Joined: 11 Sep 2009 Location: illinois Points: 87582 |
![]() ![]() ![]() ![]() ![]() |
Read "L" on the Baker unit..........
|
|
Like them all, but love the "B"s.
|
|
![]() |
|
Hubert (Ga)engine7 ![]() Orange Level ![]() ![]() Joined: 12 Sep 2009 Location: Jackson Cnty,GA Points: 6465 |
![]() ![]() ![]() ![]() ![]() |
When I was working with the fire department I ran across a lot of hydrants that checked out well above 100 psi, had a few that pushed 150 psi. Some places we could just let the pumper idle and get more than enough pressure on the lines.
|
|
Just an old country boy saved by the grace of God.
|
|
![]() |
|
FREEDGUY ![]() Orange Level Access ![]() ![]() Joined: 15 Apr 2017 Location: South West Mich Points: 5396 |
![]() ![]() ![]() ![]() ![]() |
Fire hydrants are one thing, and I would hope they have massive PSI, residential PSI is a different animal
![]() |
|
![]() |
|
Kansas99 ![]() Orange Level Access ![]() Joined: 26 Feb 2015 Location: W Kansas Points: 4867 |
![]() ![]() ![]() ![]() ![]() |
Same water main as residential. ![]() My younger brother is the very last farm on rural water and there is a water pressure regulator in the basement depending the day pressure will easily excede 100psi coming in. He's 20 miles from the pump station and 9 miles from the booster tower. |
|
"Thank you for your service Joe & the Ho"-----Joseph Stalin
|
|
![]() |
|
steve(ill) ![]() Orange Level Access ![]() ![]() Joined: 11 Sep 2009 Location: illinois Points: 87582 |
![]() ![]() ![]() ![]() ![]() |
A lot of the "pressure" depends on where you are located ( vertically) from the water tower.... every 2 ft of height is about 1 psi ... you live in the valley you got pressure.. You live on top of the mountain, you got not much....
and yes. BOOSTER stations are used to push if your going longer distances thru the country / rural areas.
|
|
Like them all, but love the "B"s.
|
|
![]() |
|
GARY(OH/IN) ![]() Orange Level ![]() Joined: 19 May 2010 Location: Findlay,Ohio Points: 917 |
![]() ![]() ![]() ![]() ![]() |
I have read somewhere and also heard on Gary Sullivan's home repair show out of Cincinnati that municipal water systems are only required to maintain at least a water pressure of 20 psi. Federal EPA law I believe. I own a mobile home park with a well and recall receiving paperwork from the EPA wanting me to notify them if the pressure ever fell below 20 psi. Any shut downs for maintenance are posted in a daily log book. I run at 30-50 psi and believe 90+ psi would create leaks bigtime. Scares me!
|
|
![]() |
|
naylorbros ![]() Bronze Level ![]() Joined: 14 Sep 2009 Location: West Jordan, UT Points: 104 |
![]() ![]() ![]() ![]() ![]() |
The pressure coming into my school before the pressure regulator runs usually between 125 and 130. At home we have several of the Woodford Y34 IOWA hydrants. I would no buy anything else
|
|
![]() |
|
plummerscarin ![]() Orange Level Access ![]() Joined: 22 Jun 2015 Location: ia Points: 3902 |
![]() ![]() ![]() ![]() ![]() |
20psi is minimum requirement in any plumbing code. Things go sideways when adding in elevation and distance. The city I work in has fluctuations to both extremes. Add booster pumps to some homes then pressure regulators to others.
|
|
![]() |